Why Doesn't Total UM Add Up? - CX-Programmer

Modified on Sun, 11 May, 2025 at 10:44 PM

Sometimes the values shown on the CX-Programmer "Memory View" dialog do not seem to add up correctly, for example 5 + 4091 does NOT total 6144:
 
This is actually due to a more complex PLC algorithm than the dialog can display. In the example above, the PLC correctly has a maximum of 6144 words. This is shared between Program memory (which can have a maximim of 4096 words) and Comment memory (up to 5K words).
 
So this dialog correctly reports that the free UM for Program use is still 4091 words, and implies that there is still a minimum of 2053 words (6144 - 4091) left for Comment memory too. This simplifies the headline figure of available Program memory.
 
Note: This issue only affects CP1MA, CPM2* and CPM2*-S* PLC models
 

Was this article helpful?

That’s Great!

Thank you for your feedback

Sorry! We couldn't be helpful

Thank you for your feedback

Let us know how can we improve this article!

Select at least one of the reasons
CAPTCHA verification is required.

Feedback sent

We appreciate your effort and will try to fix the article